Earthing CPC from TN-C-S ( PMS ) supply to shed

Anonymous user 01/03/2024 - 2.49 PM

I have a big shed and its going to be used as an electronic repair workshop. Going to have some soldering equipment , low wattage led lighting , some low wattage test equipment and a 2kw heater . The cable run by SWA Cable would be 70ft ( 21.33) Meters from consumer unit and I was wondering since the supply in the house is a TN-C-S ( PME ) supply, would the length permit using the CPC earthing from the house to the shed via the armour on the SWA Cable, or would I have to make the shed a TT supply and use a suitable earthing rod which would keep the earthing potential separate from the house earthing . Many thanks

Are you a tradesperson and able to answer this question?

5 Answers

Electrical Safety Services

Rating: 5 out of 5
Dereham
The question can only really be answered by the technical services department of the Distribution Network Operator (DNO) area that you're in. However as a general rule, due to the risk of loss of neutral under fault conditions, it would be better to have a two core SWA running to the shed and an RCD with a local earth rod at the shed end.
Answered6 January 2014
3

kevin cassidy building contractors

Rating: 5 out of 5
Accrington
22mtrs is not a long run at all and should be perfectly OK to operate as a normal radial supply off of your D-B dependant on earth loop readings of course This would be notifiable works also to be pre notified to LABC or carried out by a registered electrician to be compliant as per part P regulations as I am sure you already know. from the information you have above this will be OK run in 3core 6mm SWA protected by a 32A MCB at the distribution board DB2 with 6A+20AMCB's at the workshop. (lighting being negligable option to uprate 20A to 32A) Do not forget the requirement for RCD protection.
Answered6 January 2014
2

AJS Electrical Services

Rating: 5 out of 5
Shrewsbury
If the area has no extraneous conductive parts (Metal water pipes etc) then I would use the earth supply from SWA. I doubt you will achieve the same earth fault loop reading from the earth rod as you would from a TNCS system. Have a Google search on the topic, you will find many mixed opinions! regards
Answered7 January 2014
1

Emelec Electrical Services

Rating: 5 out of 5
Wirral
If its a true PME supply (supply authority may confirm this) then I would treat the shed supply as a TT system,
Answered6 January 2014
0

SSEC

Rating: 5 out of 5
Falmouth
You are not allowed to distribute TNC-S outside the equipotential zone so unless attached to the house sheds must be TT if its a TNC-S supply The usual way is to earth the armour on the cable with the PME then break this and ~TT it at the shed. But please get a professional to do it, if you didn't know the answer then you don't have the skill to do the job.
Answered10 January 2014