Ariston Combi A 24 MFFi Boiler - Hot Water

Anonymous user 28/02/2024 - 3.00 PM

I have an Ariston Combi boiler that is approximately 6 years old. At present I am struggling to get a decent flow of hot water. Based on some crude testing, I can achieve 40C at a flow rate of 2.4 litres/min or 30C at 6 litres/min. The setting on the boiler is at its maximum setting of 60C. Also, the central heating is working well. Please could you suggest what the problem may be and what I should do about it. Many thanks, Kenneth

Are you a tradesperson and able to answer this question?

1 Answer

JMS plumbing and heating

Rating: 5 out of 5
Corsham
Hi Kenneth Normally when you have low temperature and low flow rates, it would indicate that the domestic heat exchanger is scaled up. They are a plate heat exchanger on that model so very likely that is the problem.
Answered1 March 2014