Does a combi boiler need a bigger gas pipe than boiler with large water tank?
Anonymous user 28/02/2024 - 2.57 PM
Have had a couple of plumbers round to quote for a new boiler we want putting in - it would mean changing from a boiler with a large water tank to a combi boiler. One has said that the pipe coming from the gas meter is a 22mm and the pipe going into the boiler is only 15mm so the 15mm section needs to be replaced which involves pulling all my carpets and floors up to find the join. The other guy didn't even mention it. So who is right? Do I need the larger pipe to supply a combi or not? Forgot to mention, its a Worcester Bosch CDI Compact 32. Thanks
Are you a tradesperson and able to answer this question?
4 Answers
Anonymous user
A 'combi boiler' would draw off more gas in a shorter period of time as the hot water is instantaneously heated, as opposed to a 'heat only' or 'system boiler' where they would heat a HW cylinder over a period up to an hour. Little behold to upsize a 15mm gas pipe to 22mm or even 28mm is not a difficult job. Hope this helps. DC Plumbing & Heating
Answered28 December 2014
10
Boiler Homecare
Rating: 5 out of 5
You have not mentioned the make & model of the proposed boiler, so we cannot answer your question. But the majority of new condensing combi boilers do require a 22mm gas feed. Just because the other installers did not mention this then they may have over looked this important factor.
The installer(s) should as good practise when quoting to renew your boiler carry out a gas pipe sizing exercise, to ensure no one gas appliance is starved of gas when all appliances are running simultaneously. Ask the installer who stated the increase of gas pipe if he did indeed carry out this exercise, if necessary?
Based on the updated information of your proposed boiler it does require a 22mm gas feed. You can easily check this out by simply ringing Worcester Bosch technical support.
Answered7 June 2013
8
Anonymous user
The Worcester 32 compact would need a 22mm supply pipe and possibly upgrade the pipe from the meter to 28mm depending on what appliances you have in your property. The allowed drop for a Worcester 32 is 2.5mb from the meter to the inlet pressure at the boiler with appliances working.
Answered4 March 2014
8
PAUL CATON GAS & OIL SERVICES LTD
Rating: 5 out of 5
The Worcester 32 compact would need 22mm pipe running to it and may even need to upgrade the gas supply to 28mm dependant on distance and other appliances which are also on the supply.
Answered10 February 2014