what size cable is ok for an old belling electric range cooker?
Anonymous user 23/02/2024 - 2.45 PM
What size cable is ok for conecting an electric range cooker? We have an old house with only a 6mm cable x2 in our kitchen. Both on opposite sides of the kitchen, one for the old hob and other for the oven. Advice please.
Are you a tradesperson and able to answer this question?
4 Answers
Anonymous user
I'm sorry but that is not right, 15kW is nearly 63amps. Usually like you said it's normally protected by a 30 or 32 Amp circuit breaker but it all depends on the demand of the actual appliance.
Answered3 June 2013
4
kevin cassidy building contractors
Rating: 5 out of 5
The rating of the circuit is determined by the assessment of the current demand of the cooking appliance(s), and cooker control unit socket outlet if any, in accordance with Table A1 of appendix A. A 30 or 32A circuit is usually appropriate for household or similar cookers of rating up to 15KW.
ADDITIONAL NOTE TO RS INSTALATIONS:
The above statement has been copied word for word from the on site guide BS 7671:2008(2011) (green copy)
appendix H section H4 on page 176. These are theIET wiring regulations 17th edition all part P registered electricians are required to work to and I know it was exactly the same in the previous edition.
Here are the calculations as stated by the onsite guide.
Appendix A table A1
Household cooking appliance
The first 10A of the rated current plus 30% of the remainder of the rated current plus 5A if a socket outlet is incorporated in the control unit.
i.e. 15kw=65.217391A less 10A=55.217391x30%=16.565217
10A+16.565217A+5A=31.565217A
So according to the official calculations the original statement above is correct.
I know a lot of guys do not know this which is why I listed table A1 appendix A then carried on to do the calculations as laid out in the same guide. So feel free to check my statements in the on site guide - all electricians are required to have one.
Answered5 June 2013
3
Electrical Safety Services
Rating: 5 out of 5
You need to get the Kw rating of the oven e.g 9kw and convert this to watts (9000) and then divided this by the voltage of 230v this will give you the current drawn under full load. Once you know this its then possible to assess if 6mm cable is adequate or not, but with two appliances connected to it, 10mm cable would be the best option.
Answered3 June 2013
3
E3 Electrical
Rating: 4.9 out of 5
So much rubbish is talked about cooker circuits with well-meaning electricians treating them as if they are showers.
With cooker circuits, you have to apply diversity as Kevin Cassidy has the other two answers here are not right, a 6mm cable can generally be sufficient for up to15 kW of cooking facilities as found at H4 page 212 of the current onsite guide.
Answered10 November 2023