electric cooker socket
Anonymous user 03/03/2024 - 2.59 PM
My contractor has hidden the socket behind a false panel, so the socket is not accessible. Is this legal?
Are you a tradesperson and able to answer this question?
2 Answers
Electrical Safety Services
Rating: 5 out of 5
No it is not complaint with BS7671:2008 wiring regulations and would be recorded as a C3 defect on any electrical inspection, as the wiring regulations require that the cooker isolator switch is readily accessible and that it can be quickly isolated in the event of an emergency and/or for mechanical maintenance/repair of the cooker.
If your contractor has issued a certificate for the work (and there should be two certs for this work as its in a kitchen!) its worth checking to see what comments he has put in the "Departures from Regulations" box.
Answered27 May 2013
1
kevin cassidy building contractors
Rating: 5 out of 5
Does your definition of not accessible mean you need tools to access it. Also do you mean the isolator or the outlet?
Answered27 May 2013