Is 6mm cable with a 40 amp MCB sufficient for a 8.5 kw electric shower?
Anonymous user 23/02/2024 - 3.11 PM
I was told by a BG engineer that my 6mm cable to my 8.5 KW electric shower needs to be replaced by 10mm cable because it runs through wall insulation. I was also told that the 40 amp MCB is too high and needs to be replaced. I have done the calculation of 8500W divided by 240V, I get 35.4 amps so surely a 32amp MCB would be too low and keep tripping. I understand the next one up is the 40 amp MCB which is the one I already have! Is the engineer trying to get a job to replace the 6mm cable when it is not necessary, or is he correct in saying that I need to have a 10mm cable?