Can I use 1mm 3 core & earth to connect sockets

Anonymous user 09/03/2024 - 2.45 PM

I'm doing first fix, I.e getting all the cables in the right place for some new light fixings. Can I use 1mm 3 core & earth to connect 2 x 2 way switches? Also for wiring switch to 3 spotlights should I use 1mm or 1.5 t&e?

Are you a tradesperson and able to answer this question?

2 Answers

Lee Foster Services Ltd

Rating: 4.6 out of 5
Bristol
Yes, 3 core is required for 2 way lighting circuits. Personally i always use 1.5mm t&e for lighting, but either 1mm or 1.5mm is ok. With the use of LED lighting so much these days, the load on lighting circuits is far less than previously used, However i would always advise you to plan the intended potential load that may be used, and use the correct size based upon this. Hope this helps.
Answered22 November 2016
1

Johnson Electrical (Dorset) Ltd

Rating: 5 out of 5
Broadstone
Hi Tim, yes you can use 3 core for the 2 way, infact you need 3 cores or it wont work as a two way, & you can use 1.0mm t&e for the lighting, for up to 1000w or 1 kw (6A,) as your only connecting up 3 lights ( max 150w,) you will be fine, 1.5mm t&e can take more watts/kw, sould you want to run more than 6A/1kw, genrally not needed on domestic installs..............hope this helps.
Answered22 November 2016
1