Skip to main content

Ready to hire?

Post your job in minutes, browse real reviews and choose who to speak to.Post a job

Need some tips or advice?

Ask a question
Plumbing

Remeha avanta plus boiler error code E10 - no hot water or heating

Anonymous user 23/02/2024 - 3.01 PM

I have the above boiler 24c and the error code E10 is flashing up. This has occurred after I bled a radiator since the heating system was getting very noisy. I can't get the boiler to work now and have a one year old baby so need hot water and heat! Any advise how to rectify the E10 error?

Are you a tradesperson and able to answer this question?

1 Answer

kevin cassidy building contractors

Rating: 5 out of 5
Accrington
E10 Indicates no flow through the boiler on the venting cycle often associated with refilling or installing of the Remeha Avanta boiler. Check for minimum water pressure. Check that the pump is working and or has been correctly installed and wired. Check that the boiler and the system have been filled and vented properly
Answered10 March 2016
22