Hi,
My electician has rewired the house and installed a 4.2kW oven (with a separate gas hob). The oven radial uses a 2.5mm wire with a 20 amp fuse, and the length of the wire from the consumer unit to the oven is about 4m. My builder has told me that the 2.5mm wire is unsafe, but my electrician insists it's okay because the oven has no hob. Can anyone confirm whether the 2.5mm wire is safe and compliant with the regulations?
..................
Thanks all, much appreciated.
5 Answers from MyBuilder Electricians
Best Answer
Scarning • Member since 17 Oct 2011 • 696 jobs, 100% positive feedback
Builder normally equals BODGER! they are some of the biggest cowboys going and should not be touching or even commenting on electrical matters, as 99% of them are not electrically competent and have not undergone formal electrical training or hold relevant qualifications. Where as most Part P registered electricians do.
A 4200 watt (4.2Kw) oven at 230volts (4200 divided by 230 ) = 18.26 amps. A 2.5mm cable is capable of supplying around 23-25 amps depending on the method of installation, so is fine, safe and compliant on a 20amp circuit breaker. Its very clear that the builder is not an electrician and probably knows little or nothing about circuit design and calculating circuit current. If he did then he could have done this quick calculation and realised it was perfectly compliant with BS7671:2008.
Answered 10th Apr 2014
Hengoed • Member since 14 May 2012 • 85 jobs, 98% positive feedback
Hello,
A quick calculation for your problem:
A 4.2kw oven =4200w
4200/240=17.5amps
A 2.5mm short length of cable without diversity applied for insulation etc is capable of 24amps
Therefore your 2.5mm cable over the short distance IS SUITABLE for the capacity of the oven.
The 20amp fuse is the correct size fuse.
But in doubt always consult your ovens manual on there MINIMUM specification for electrical conections.
I hope this helps you.
Leighton Haynes
Answered 10th Apr 2014
kevin cassidy building contractors
Accrington • Member since 16 Dec 2010 • 45 jobs, 100% positive feedback
You have not given the method of installation, they are as listed below. Your builder is only quoting from limited knowledge that generally cooker supplies are run in 6.0mm T+E and does not know how to calculate the requirements. It sounds like your electrician has taken the cable to its design limit if using method B or C which is acceptable.
2.5mm T+E
Installation method A (enclosed in conduit in a thermally insulating wall, etc)
current carrying capacity 18.5A (max MCB 16A)
Installation method B (enclosed in conduit on a wall or in trunking, etc)
current carrying capacity 23.0A (max MCB 20.0A)
Installation method C (clipped direct)
current carrying capacity 27.0 (max MCB 20.0A)
Answered 10th Apr 2014
Pontypridd • Member since 11 Nov 2010 • 5 jobs, 100% positive feedback
Your electrician is right. The cooker will pull a max of 18amps and the cable is rated at around 24amps and protected by 20amp fuse so your good to go : )
Answered 10th Apr 2014
Western ELectrical Installations
Caerphilly • Member since 31 Mar 2010 • 247 jobs, 100% positive feedback
hi
4200w divided by 230v = 18.26 amps
from memory 2.5 t and e in normal conditions can carry apprx 27 amps
so :
cable is rated at 27amps
fuse is rated at 20amps
oven is rated at 18amps
the numbers look fine to me , however there are other things to consider.
i.e if the cable run travels through more than 400mm (depth) of thermal insulation the current carrying capacity of the cable has to be halved so the cable will become the weakest link in the chain.
are there other issues the builder has noticed that you have not posted?
best regards
Answered 10th Apr 2014
Related Questions
-
Switch for Electric Oven goes OFF and oven & ignition for gas hob doesn't work
We have an integrated Electric oven and Gas hob. The electric oven and the ignition for the Gas Hob suddenly stopped working....
-
Wiring for a Bosch oven
We have recently installed a Bosch oven...
-
Max power boost 4.6kw Hob + 3.2kw Oven connecting to a 2.5mm wire with 20amp switch and 20amp fuse
Hi am planning to install an 3.2kw oven and currently there's only 1 power outlet which is connecting to my max power boost...
-
Correct installation for a built in combination microwave oven and a separate oven.
Both units are manufactured by Siemens. Fault occurred on combi microwave called Siemens and two service engineers came to carry...

Post your job to find high quality tradespeople and get free quotes
Question Categories
- All Questions
- Architectural Services
- Bathroom Fitting
- Bricklaying
- Carpentry & Joinery
- Carpet & Lino
- Central Heating
- Chimneys & Fireplaces
- Conservatories
- Conversions - General
- Damp Proofing
- Demolition & Waste Clearance
- Driveways
- Electrical
- Extensions
- Fascias, Soffits & Guttering
- Fencing
- Gas Work
- Groundwork & Foundations
- Handyman
- Hard Flooring
- Insulation
- Kitchen Fitting
- Landscape Gardening
- Locksmiths
- Loft Conversions
- New Builds
- Painting & Decorating
- Plastering
- Plumbing
- Restoration & Refurbishment
- Roofing
- Security Systems
- Stonemasonry
- Tiling
- Tree Surgery
- Windows