2.5mm wire for 4.2kW oven
Anonymous user 28/02/2024 - 3.03 PM
Hi, My electician has rewired the house and installed a 4.2kW oven (with a separate gas hob). The oven radial uses a 2.5mm wire with a 20 amp fuse, and the length of the wire from the consumer unit to the oven is about 4m. My builder has told me that the 2.5mm wire is unsafe, but my electrician insists it's okay because the oven has no hob. Can anyone confirm whether the 2.5mm wire is safe and compliant with the regulations? .................. Thanks all, much appreciated.
Are you a tradesperson and able to answer this question?
5 Answers
Electrical Safety Services
Rating: 5 out of 5
Builder normally equals BODGER! they are some of the biggest cowboys going and should not be touching or even commenting on electrical matters, as 99% of them are not electrically competent and have not undergone formal electrical training or hold relevant qualifications. Where as most Part P registered electricians do.
A 4200 watt (4.2Kw) oven at 230volts (4200 divided by 230 ) = 18.26 amps. A 2.5mm cable is capable of supplying around 23-25 amps depending on the method of installation, so is fine, safe and compliant on a 20amp circuit breaker. Its very clear that the builder is not an electrician and probably knows little or nothing about circuit design and calculating circuit current. If he did then he could have done this quick calculation and realised it was perfectly compliant with BS7671:2008.
Answered20 September 2025
184
Anonymous user
Hello,
A quick calculation for your problem:
A 4.2kw oven =4200w
4200/240=17.5amps
A 2.5mm short length of cable without diversity applied for insulation etc is capable of 24amps
Therefore your 2.5mm cable over the short distance IS SUITABLE for the capacity of the oven.
The 20amp fuse is the correct size fuse.
But in doubt always consult your ovens manual on there MINIMUM specification for electrical conections.
I hope this helps you.
Leighton Haynes
Answered10 April 2014
83
kevin cassidy building contractors
Rating: 5 out of 5
You have not given the method of installation, they are as listed below. Your builder is only quoting from limited knowledge that generally cooker supplies are run in 6.0mm T+E and does not know how to calculate the requirements. It sounds like your electrician has taken the cable to its design limit if using method B or C which is acceptable.
2.5mm T+E
Installation method A (enclosed in conduit in a thermally insulating wall, etc)
current carrying capacity 18.5A (max MCB 16A)
Installation method B (enclosed in conduit on a wall or in trunking, etc)
current carrying capacity 23.0A (max MCB 20.0A)
Installation method C (clipped direct)
current carrying capacity 27.0 (max MCB 20.0A)
Answered10 April 2014
65
DGM Electrical
Rating: 5 out of 5
Your electrician is right. The cooker will pull a max of 18amps and the cable is rated at around 24amps and protected by 20amp fuse so your good to go : )
Answered14 November 2025
40
Western ELectrical Installations
Rating: 5 out of 5
hi
4200w divided by 230v = 18.26 amps
from memory 2.5 t and e in normal conditions can carry apprx 27 amps
so :
cable is rated at 27amps
fuse is rated at 20amps
oven is rated at 18amps
the numbers look fine to me , however there are other things to consider.
i.e if the cable run travels through more than 400mm (depth) of thermal insulation the current carrying capacity of the cable has to be halved so the cable will become the weakest link in the chain.
are there other issues the builder has noticed that you have not posted?
best regards
Answered14 November 2025