Anonymous user 28/02/2024 - 3.05 PM

I want to install a new Zanussi oven. The old oven was wired into a 13A fused spur (behind the unit) that came off a cooker isolator / switch located above. This is in its own RCD protected circuit. The new oven hasn't come with any wires just a black plate at the back to connect the L,N and earth into. I've replaced the cooker isolator / switch with a new one. This has a 45A fuse for the cooker isolator. My question is, do I need to wire the new oven through the 13A fused spur again or can I remove that entirely and safely wire the oven directly to the 45A fused cooker isolator/ switch. Secondly, if I decide to keep the 13A spur and wire the oven off that, can I also wire in the power to the 3A ignition for the gas hob? Edit: the kW max of the oven is 2,780-2,550 so that should be fine to go through the 13A unswitched fused connection unit. Regarding the hob - this has come wired with a non-rewireable 3A fused plug. I really don't want to cut off the plug to wire it into the connection unit. I was thinking the best thing to do would be to wire a 13A plug onto the oven and replace the 13A unswitched fused connection unit with a 2 gang DP switched plug socket, relocate that to the adjacent unit for ease of access and then just plug both the oven and the hob into that. Does that sound legit?

2 Answers

kevin cassidy building contractors

Rating: 5 out of 5
Accrington
You have made no mention of the max load for your new oven which is the most important thing but if max load comes in under 2.9kw then you can connect the oven to a 13A fused spur but located in an adjacent unit or above the work top not behind the oven as the fuse should ideally be accessible without having to remove the oven. Failing this the MCB at the board can be down rated to a 16A (best done by an electrician). Check the fitting instructions for any specific fitting requirements. If in doubt about any electrical work seek the advise of an electrician. Secondly. The hob ignition can also be connected to this But ideally fused at 3A 2gang DP switched socket in adjoining cabinet fed from cooker outlet will be fine. Presuming MCB protectionto be 32A the minimum sise T+E to the 2g socket should be 4mm T+E unless reduced to 20A/16A then you could use 2.5MM T+E I would use butyl heat resistant 2.5mm2 cable from the plug to oven but minimum requirement for cable should be in manufacturers installation instructions. As stated above check fitting instructions.(They may allow 1.5mm heat res cable)
Answered9 August 2014
20

Knights and Regals Electrical Ltd

Rating: 5 out of 5
Manchester
Good evening, Depanding on your new oven kw, (we dont know the wattage on it) you actually cant use the 13amp fuse spur for your new oven. because normally if the cooker is rated more then 13amp they cant come prewire. If you can, remove the 13amp fuse spur and make it a cooker outlet, you might have to change the metal box with a deep one. So your wires will come from switch to cooker outlet and from cooker outlet to your oven.( cooker outlet is like a jucntion box to connect the wires coming from oven and coming from the switch). I hope this will help you do it properly. regards, Kashif
Answered8 August 2014