Overflow from Combi Boiler runs when boiler comes on, is this a problem?

Anonymous user 03/03/2024 - 2.56 PM

Just lately when the boiler comes on in the mornings, water runs from the overflow for a minute or two and then drips for about another 5 minutes. Does this mean there is a problem with the boiler?

Are you a tradesperson and able to answer this question?

2 Answers

mlmorris plumbing&heating desgin

Rating: 5 out of 5
Chingford, London
the problem is the boiler could over pressurised . on the press gage it should be set at 1.5bar if it gos to 3 bar it will discharge though the pressure felief valve.
Answered10 November 2012
1

Anonymous user

sounds like it could be the expansion vessel, if cold pressure is about 1.5 bar it should not vent any water when it heats up.
Answered12 November 2012
1