There is not a simple answer to this question,
The engineer that attend this breakdown would acess is it is a kettling noise or a hammering noise.
If it is a kettling noise it would be worthy to check the waterways of the condensate. Condensate supmp, all pipe of the condensate inside boiler, condensate trap and condensate pipe.
If it is a hammering noise, it may be possible to clean it with the powerflushing machine, if it is a one-pipe-in and one-pipe-out main heat exchanger. However if it is main heat exchanger built with a manifold and several pipes in parallel, then it is pointless to use the powerflushing machine because the cleaning product would circulate freely through those pipes that are not blocked.
It is beneficial in any case to install a magnetic filter after the repair/replace of the main heat exchanger, and it is necessary in order to learn what caused the problem,so it will not break the new main heat exchanger, to examine the type of dirtiness that your system have, is it black colour ?, that would be ferrotite sludge, and the best course of action would be to powerflush the system and treat it with corrosion and scale inhibitors, before installing the new main heat exchanger. Is it a red-orange colour sludge ?. In that case the problem may be due to constant fresh water entering in the system, for example a gravity system with header F&E cistern, indication that the system is losing water, and this have to be repaired otherwise in time the new heat exchanger will break as well.