Earthing a new consumer unit

Anonymous user 3 March 2024 - 3.43 PM

I had a an electrician to give me a quote for a new consumer unit. He told me that in order to comply with new regs, I would need a new earth to the main water(right round the house) This would involve drilling through 2 walls and running about 15 metres of earth cable. My existing fusebox is earthed to the steel gas main. What do you advise?

Are you a tradesperson and able to answer this question?

6 Answers

KRT Electrical and Property Services
KRT Electrical and Property Services
Rating: 4.7 out of 54.7570 reviews
Colchester
All incoming services whether they are Gas, Water or Oil require equipotential bonding which need to be routed back to an M.E.T (Main earthing terminal) which can be within or external to the consumer unit. This is a requirement of the wiring regulations and ensures that anything providing a route to earth is of the same potential. The only time this is not required is if the incoming service uses a plastic incoming pipe as this obviously does not provide a path to earth. I hope this brief explanation helps. Best regards Kev @ KRT Electrical Services
Answered26 July 2022
5

Anonymous user

Check whether you have a plastic blue MDPE water pipe coming in to the house. If you do you don't need any bonding to the water pipe.
Answered26 July 2022
1

StrangLX
StrangLX
Rating: 5 out of 55584 reviews
Broadstairs
Sounds like you have been given good advice, anyone quoting without checking this isn’t doing it right. Metallic gas or water services must have equipotential earth bonding installed within 600mm of where the pipe enters the property or within 600mm of the gas meter (customer side) and within 600mm of the main water stopcock. If the stopcock is some way into the property it is preferable to site the bond where the pipe enters the property. This as far as is reasonably practicable should be done before any branches in the pipework and in a location where it is easily accessible for testing and maintenance purposes. A plastic water service need not be bonded but only if it can be proven by way of testing that internal metallic pipework does not introduce an earth potential, the regs suggest it may be preferable to bond internal metallic pipework supplied from a plastic service where this cannot be proven.
Answered27 July 2022
1

Anonymous user

In contrary to most comments if the installation is in 4mm which I assume it is given the case. Then the installation stays to the regulation on which it was put in yes regulations state 10mm bonding and 600mm or before first T or elbow but during the original install if it requires 4mm and they installed nearest practice at the time then it's fine unless you change the characteristics of the properties means of power (change the mains board) if there is decent continuity on the bonding what is in and you haven't changed the mains board you aren't bound by law to have it installed.
Answered27 July 2022
1

Dc decorating services
Dc decorating services
Rating: 5 out of 55565 reviews
Stevenage
The water pipes and gas pipes need to be bounded where they come into the house
Answered25 July 2022
0

ELITE ELECTRICAL INSTALLATION SERVICES LTD
ELITE ELECTRICAL INSTALLATION SERVICES LTD
Rating: 5 out of 5552 reviews
Doncaster
If you were to upgrade the consumer unit then the earthing of any incoming metallic services (Gas, water, oil, metal structure) would have to be upgraded to 10mm if not already in 10mm. The reason for this is to keep all extraneous metal parts at the same potential. The electrician who quoted for you is correct.
Answered28 July 2022