My boiler not filling up

Anonymous user 9 March 2024 - 3.27 PM

The pressure on my boiler is low I have tried topping it up but the pressure gauge is not moving and I can't hear the water going into my boiler when I switch the water gauge on Thanks Alan

Are you a tradesperson and able to answer this question?

6 Answers

The Young Group Ltd
Rating: 4.8 out of 54.8534 reviews
Newton Aycliffe
Hi Alan, Ensure you have water to the taps to make sure your waters on. Also check the return is open on the boiler. If both of them are correct then your expansion vessel will need recharging/replacing.
Answered27 February 2022
6

Rota Gas Heating & Plumbing
Rating: 5 out of 5551 review
Lincoln
Make sure that both valves are open on the filling loop and tht you have running cold water at the tap. If this is ok, you may have a stuck closed none return valve on the filling loop or a faulty pressure gauge on your boiler
Answered10 March 2022
2

Anonymous user

Hi keep on the pressure on gauge it’s takes more time to show you changes on the water pressure cheers
Answered27 February 2022
1

Plumb Tidy Ltd
Rating: 5 out of 555117 reviews
Caerphilly
In addition to the previous answer, ensure both valves on the filling loop are open if you have two and make sure you are using the correct valves as some people I know try operating the return valve thinking it’s the filling loop. But as mentioned before check water to the taps to ensure you have water. If still no joy a plumber/heating engineer will take a look as it maybe several other things.
Answered18 March 2022
1

David Lloyd Plumbing Services
Rating: 5 out of 5553 reviews
Southport
Just because a valve seems open it might not be open due to age if valve being seized due to calcium deposits around the valve or just to age and depreciation of the valves.
Answered18 March 2022
0

Fred Martin Plumbing and Heating
Rating: 5 out of 555429 reviews
Purley
I would check you have water in your heating system as the pressure gauge could be faulty due to debris in system. If all ok you will need to check for leaks. Check Pressure relief valve pipe discharging to outside which is 15mm copper?
Answered18 March 2022