What distance from the bottom of a fire door to the floor is allowed?

Anonymous user 17 October 2018 - 10.29 AM

We have a fire door that we had trimmed down when we got a carpet fitted. How big a gap is allowed at the bottom for it to pass fire safety tests? And does an intumescent strip need fitting underneath?

4 answers from MyBuilder tradespeople

APG Plumbing & Heating
Best answer
APG Plumbing & Heating
Rating: 5 out of 5555 reviews
Doncaster

British standards (BS9999:2008) recommends for fire doors with cold smoke control that the threshold gap should be either less than 3mm in height or should be fitted with a threshold seal.

Answered

17 October 2018

Like

1
Harwood Projects

No reviews yet

Bury

I would leave a gap no greater than 8mm from the bottom of a fire door, unless you require smoke control doors then 3mm and fit a threshold smoke seal. Hope this helps :-)

Answered

17 October 2018

Like

1
PH 1066 Construction Ltd
Rating: 5 out of 55517 reviews
Pevensey

Underneath the fire door, a gap of 8mm is traditionally acceptable, although for fire doors that are required to limit spread of cold smoke only 3 mm is permissible with a threshold seal to be fitted if the gap is bigger.

Answered

17 October 2018

Like

1
S&D Joinery
Rating: 5 out of 5555 reviews
Sutton In Ashfield

The gap between the bottom of the fire door to the floor should be between 6 mm to 8 mm the meet that right fire regulations