Anonymous user 17 September 2011 - 8.06 PM

Hi there, We are in the process of adding a single-storey extension to our house. Both have cavity walls but the builder has used wall plates to connect the two walls without actually opening the existing cavity to make the new and old cavities continuous. No damp-proof membranes appear to have been used either. It does not appear to be required by building regs but is this best/recommended practice? The new walls are now at roof height and the carpenter has already started on the roof rafters. Any advice gratefully received.

Are you a tradesperson and able to answer this question?

6 Answers

Best answer
James White Brickwork
Rating: 4.7 out of 54.7579 reviews
Morpeth
If i have understood correct. There is no need to expose existing cavitys anymore to tie in, Simply, starter bars are drilled to the wall and you go from there. You do however need a stihl saw cut running up building in the cavity and a damp proof course put in place. Hope that explains a little
Answered18 September 2011

Like

20

Anonymous user

He is correct in using the wall tie system to tie in old to new, however building control in my area insist of a vertical joint cut out, central of the 2 new walls, with a disc cutter, then insert a vertical dpc, held in to chase with clear silicon.
Answered18 September 2011

Like

18

R.Hughes Building and Conservation Ltd
Rating: 5 out of 55540 reviews
Wellingborough
Hi. It is my belief that the cavities need to be continuous and uninterrupted to meet building regs. I certainly do it everytime and its something the building inspector will check. Its ok to use wall starters but is again best practise to tooth out the brickwork on the existing building to tie in the new brickwork, it looks much better and also allows you to open up the existing cavity to join it to the new. With regards to the damp proof membrane, this should have been used in the floor and then overlapped to tie in with the damp proof course before the superstructure was built. Again, this is essential and will be picked up by the building inspector!! It might be worth having a chat with your builder to see if he has used a dpm and also whether your local building regs requires an uninterrupted cavity. Then get the building inspector out to check that he is happy with everything so far before you go any further. Hope this helps. Rick
Answered18 September 2011

Like

14

Anonymous user

Your builder should, at the very least,have cut a slot through the existing wall and inserted a vertical DPC. Ideally, he should have opened the wall to ensure a continuous cavity. What has your architect specified in the construction notes? Without a DPC or cavity there is a risk of damp penetration. This is something you should take up with the builder, as it shows lack of care and may be a pointer to sloppy work on other parts of the build. Also ensure that all required Building Control Inspections are carried out, or you may struggle to get a completion certificate.
Answered18 September 2011

Like

13

Anonymous user

Usually it is ok not to open the cavity as this can weaken the wall ,as long a you fit a vertical damp course. To do this you need to run a cutter up the wall were the cavity would be then slot in the damp course,if you have any questions or your unhappy you could check with the building inspector he is there to help you and the builder if needs be . Hope this helps
Answered18 September 2011

Like

9

Anonymous user

Not sure without seeing your house, but if the extension is single story there should be cavity trays in the existing wall above the roof. This is to stop penetrating damp (i.e from driving rain) above the roof from running down the cavity and dampening the now internal cavity wall inside.
Answered5 December 2011